EICR - main earth and neutral

Former Community Member
Former Community Member
Hi was conducting a EICR on a consumer unit today removed the cover and Main earth cable was 8 x single strand insulated cables istead of expected single 25mm also earth was the same??? it is in an apartment and has been running fine for

at least 20 years, just want to know what to input for csa?? and should I note it in observations under C3 CODE???? ANY ADVISE WELCOME THANKS
Parents
  • davezawadi (David Stone):

    Another example. Now discuss if this is permitted because I won't.




    You have already discussed it and the answer isn’t clear cut.

    https://communities.theiet.org/discussions/viewtopic/1037/25616


    I asked where the meter is with the intention of trying to determine if the cable should be classified as suppliers equipment or part of the consumers installation, the next question is what fuses are installed to protect this cable, is protected by the suppliers fuse or a fuse within the consumers installation?


Reply
  • davezawadi (David Stone):

    Another example. Now discuss if this is permitted because I won't.




    You have already discussed it and the answer isn’t clear cut.

    https://communities.theiet.org/discussions/viewtopic/1037/25616


    I asked where the meter is with the intention of trying to determine if the cable should be classified as suppliers equipment or part of the consumers installation, the next question is what fuses are installed to protect this cable, is protected by the suppliers fuse or a fuse within the consumers installation?