EICR - main earth and neutral

Former Community Member
Former Community Member
Hi was conducting a EICR on a consumer unit today removed the cover and Main earth cable was 8 x single strand insulated cables istead of expected single 25mm also earth was the same??? it is in an apartment and has been running fine for

at least 20 years, just want to know what to input for csa?? and should I note it in observations under C3 CODE???? ANY ADVISE WELCOME THANKS
Parents
  • One end of this cable has to connected to a meter, I would like to see how this has been done.


    The manufacturer’s state on their data sheets that the neutrals are coated with a polymeric compound and I am not convinced that is true insulation.


    If the cable insulation is tested at 500 Vdc will it pass?
Reply
  • One end of this cable has to connected to a meter, I would like to see how this has been done.


    The manufacturer’s state on their data sheets that the neutrals are coated with a polymeric compound and I am not convinced that is true insulation.


    If the cable insulation is tested at 500 Vdc will it pass?