Sparkingchip:gkenyon:
It's entirely possible (and perhaps more likely) that a line to neutral or line to earth fault will only short line to a single strand of the neutral or earth (or perhaps a few strands).
A highly likely scenario is that a carpenter fires a nail from a nail gun into a concealed cable, it would almost certainly only contact two of the neutral conductors and the whole of the live conductor, bear in mind there’s possibly nineteen neutral conductors so that gives an effective neutral of say 2.6 mm.
Agreed - and yes, it depends on the makeup as to the actual number and csa of the N conductors. Sounds like possibly 35 sq mm rather than the 25 sq mm example I ran through?
Sparkingchip:gkenyon:
It's entirely possible (and perhaps more likely) that a line to neutral or line to earth fault will only short line to a single strand of the neutral or earth (or perhaps a few strands).
A highly likely scenario is that a carpenter fires a nail from a nail gun into a concealed cable, it would almost certainly only contact two of the neutral conductors and the whole of the live conductor, bear in mind there’s possibly nineteen neutral conductors so that gives an effective neutral of say 2.6 mm.