This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EICR - main earth and neutral

Former Community Member
Former Community Member
Hi was conducting a EICR on a consumer unit today removed the cover and Main earth cable was 8 x single strand insulated cables istead of expected single 25mm also earth was the same??? it is in an apartment and has been running fine for

at least 20 years, just want to know what to input for csa?? and should I note it in observations under C3 CODE???? ANY ADVISE WELCOME THANKS
Parents
  • Which page of BS7671 permits split con on the consumer's side of the meter, or under BS7671 at all? It is probably not dangerous but is not protected, the sheath does not provide much mechanical protection to the very weak N insulation, terminating the centre aluminium conductor may be difficult because of corrosion/bimettalic consideration etc. I can find no reference to BS7870 in BS7671.
Reply
  • Which page of BS7671 permits split con on the consumer's side of the meter, or under BS7671 at all? It is probably not dangerous but is not protected, the sheath does not provide much mechanical protection to the very weak N insulation, terminating the centre aluminium conductor may be difficult because of corrosion/bimettalic consideration etc. I can find no reference to BS7870 in BS7671.
Children
No Data