EICR - main earth and neutral

Former Community Member
Former Community Member
Hi was conducting a EICR on a consumer unit today removed the cover and Main earth cable was 8 x single strand insulated cables istead of expected single 25mm also earth was the same??? it is in an apartment and has been running fine for

at least 20 years, just want to know what to input for csa?? and should I note it in observations under C3 CODE???? ANY ADVISE WELCOME THANKS
Parents
  • David


    Commonly used on BNO installations from the Ryfield board to a series 8 Head fitted with a solid link red head for meter isolation. Surface run cables only for the unmetered supply to a local cut out with a red head solid link with the neutral and earth separated. It is still TN-C-S on the incoming supply cable but the neutral and earth split on the BNO network to comply with BS 7671.










Reply
  • David


    Commonly used on BNO installations from the Ryfield board to a series 8 Head fitted with a solid link red head for meter isolation. Surface run cables only for the unmetered supply to a local cut out with a red head solid link with the neutral and earth separated. It is still TN-C-S on the incoming supply cable but the neutral and earth split on the BNO network to comply with BS 7671.