EICR - main earth and neutral

Former Community Member
Former Community Member
Hi was conducting a EICR on a consumer unit today removed the cover and Main earth cable was 8 x single strand insulated cables istead of expected single 25mm also earth was the same??? it is in an apartment and has been running fine for

at least 20 years, just want to know what to input for csa?? and should I note it in observations under C3 CODE???? ANY ADVISE WELCOME THANKS
Parents
  • A CNE can be used in an installation (with certain exceptions), unless prohibited by ESQCR. For installations that take an LV supply from the DNO, combined neutral and earth is usually prohibited by ESQCR downstream of the distributor's equipment - see Regulation 8(4). This is also why, even in installations with private transformers and PNB type arrangement, effectively the only bits of TN-C are effectively the transformers / generators themselves.
Reply
  • A CNE can be used in an installation (with certain exceptions), unless prohibited by ESQCR. For installations that take an LV supply from the DNO, combined neutral and earth is usually prohibited by ESQCR downstream of the distributor's equipment - see Regulation 8(4). This is also why, even in installations with private transformers and PNB type arrangement, effectively the only bits of TN-C are effectively the transformers / generators themselves.