Compression fitting can be used on copper pipe and no solder is required.
Zoomup:
What I said was that I would not fit a B.S. 951 earthing clamp onto a lead gas pipe. Nothing more nor less.
What does the Standard have to say about the types of pipe that may be used? (I have not got a copy and have lost my library access for the time being.)
AJJewsbury:One of my concerns about using lead is its low melting point, perhaps when carrying large fault currents. Domestic lead covered cables of old were perhaps fused at 5, 15 or even 30 Amps so fault currents were relatively small. With lead pipes that may carry large diverted neutral currents the lead may melt or or best become soft, so fitting a B.S. 951 earth clamp to a lead gas pipe could be dangerous. I would never do so. Lead melts at about 300 degrees C and copper at over 1,000 degrees C.
Are you really suggesting that if you worked on an installation where all the gas pipework was all lead, you'd leave it unbonded?
- Andy.
I don't think that an all lead gas pipe system in a house would comply with modern gas regs. these days Andy.
What I said was that I would not fit a B.S. 951 earthing clamp onto a lead gas pipe. Nothing more nor less.
Z.
AJJewsbury:One of my concerns about using lead is its low melting point, perhaps when carrying large fault currents. Domestic lead covered cables of old were perhaps fused at 5, 15 or even 30 Amps so fault currents were relatively small. With lead pipes that may carry large diverted neutral currents the lead may melt or or best become soft, so fitting a B.S. 951 earth clamp to a lead gas pipe could be dangerous. I would never do so. Lead melts at about 300 degrees C and copper at over 1,000 degrees C.
I'm sure you're worrying over nothing. Copper pipework is no more resistant to heat than lead pipework - as both will fail well below 300 degrees when the solder in the joints melts. If it's not an issue with copper pipes why should it be with lead ones?
Blowlamp flame on copper pipe: pipe remains intact.
Blowlamp flame on lead pipe and it will melt.
Compression fitting can be used on copper pipe and no solder is required.
Z.
One of my concerns about using lead is its low melting point, perhaps when carrying large fault currents. Domestic lead covered cables of old were perhaps fused at 5, 15 or even 30 Amps so fault currents were relatively small. With lead pipes that may carry large diverted neutral currents the lead may melt or or best become soft, so fitting a B.S. 951 earth clamp to a lead gas pipe could be dangerous. I would never do so. Lead melts at about 300 degrees C and copper at over 1,000 degrees C.
mapj1:
Why do we worry about current in a lead sheath more or less than in a steel armour on a modern cable ? - if anything the lead has a larger cross-section, is better cooled due the larger surface area...
This American video confirms the robustness of P.I.L.C. cables.
https://www.bing.com/videos/search?q=youtube+terminating+PILC+lead+cable&docid=608021297359238224&mid=2B0334B9E1D44F83AB9D2B0334B9E1D44F83AB9D&view=detail&FORM=VIRE
Z.
mapj1:
Why do we worry about current in a lead sheath more or less than in a steel armour on a modern cable ? - if anything the lead has a larger cross-section, is better cooled due the larger surface area and and if anything paper and oil not exposed to air is likely to be more robust than XPLE insulation in terms of failure modes if it heats up.
I agree once the lead is damaged or not connected, then you have a problem, but that is true of any armoured cable.
Mike.
One of my concerns about using lead is its low melting point, perhaps when carrying large fault currents. Domestic lead covered cables of old were perhaps fused at 5, 15 or even 30 Amps so fault currents were relatively small. With lead pipes that may carry large diverted neutral currents the lead may melt or or best become soft, so fitting a B.S. 951 earth clamp to a lead gas pipe could be dangerous. I would never do so. Lead melts at about 300 degrees C and copper at over 1,000 degrees C.
Back in the 40s a device called a "Pyrotip" was used to "Burn" lead for jointing. The manufacturer was the General Electric Company of Schenectady. The heating source was electrical in the form of a step down transformer to a carbon electrode. The work was connected by a clamp to one terminal and the carbon rod to the other. The p.d. was insufficient to form an arc. The lead was melted only by the power dissipated in the carbon rod and that dissipated in the contact resistance between rod and work.
So in this case electricity traveling through the rod and lead, was a friend to melting lead, in other cases I am concerned about gas leaking from damaged lead pipes.
Z.