Zoomup:
With 2.5/1.5mm2 6242Y cable wired as a ring there are two C.P.C.s at each accessory on the ring, excepting spurs. When connecting a ring final circuit to a 4.0/1.5mm2 6242Y cable there is only one 1.5mm2 C.P.C.
Has this ever concerned anyone? Are there any potential problems?
Z.
Can't be worse than the single 1.5mm² c.p.c. on a complete 4mm²/32A radial - which is deemed acceptable (high protective conductor currents notwithstanding).
- Andy.
Zoomup:
With 2.5/1.5mm2 6242Y cable wired as a ring there are two C.P.C.s at each accessory on the ring, excepting spurs. When connecting a ring final circuit to a 4.0/1.5mm2 6242Y cable there is only one 1.5mm2 C.P.C.
Has this ever concerned anyone? Are there any potential problems?
Z.
Can't be worse than the single 1.5mm² c.p.c. on a complete 4mm²/32A radial - which is deemed acceptable (high protective conductor currents notwithstanding).
- Andy.