I was called out to a static holiday/residential caravan today. Nuisance tripping was reported. Apparently the electrics were reliable before the van was moved to a new pitch on the same sandy site. The van's consumer unit comprises 1 30mA R.C.D., a 32 Amp socket M.C.B. and a 6A lighting M.C.B.


The pitch permanent "hook up" point comprises a 30 mA R.C.D. and a 16 Amp M.C.B.


The lady has many high powered appliances, 2kW kettle, three 2kW+ room heaters, a 2.2kW coffee machine etc. The heating is normally by bottled gas.


The two R.C.D.s tested out fine, not over sensitive. But the van owner can not remember which devices tripped off over a period of time. Once the nearby brick supply building had to be accessed to reset something, but we were not allowed even just to look inside it today by the site owners. Very unhelpful.


Anyway, all appliances tested good, no faults. I presumed that the lady had plugged too many items in at once.                                                                                                                                                                                                                                                                Guidance note 7, page 58 Fig. 7.1 it shows 4 possible separate vans being supplied via a single  100 mA R.C.D.


So, looking at the possibility of nuisance tripping if 4 vans each leak say 20 to 30 mA, the 100 mA R.C.D. could trip off blacking them all out. Should a time delayed 100mA type be used? The Guidance note says that the 100 mA R.C.D. is chosen to discriminate with the pitch socket outlets R.C.D.s. But, if say 100mA was to flow from a van fault,  both the 30mA pitch socket R.C.D. AND the 100mA brick supply building could trip off together. This would then deprive a total of 4 vans of a supply.


Comments please.


Thanks,


Z.


  • Kelly Marie Angel:

    Morning guys I've re read all the posts now and realise that yesterday I was getting myself in a bit of a mess trying to understand stuff I got it now tho so my apologise for my previous confusion think its cos I didn't take my pills Lo,


    No apologies needed. If something wasn't clear to you it probably wasn't clear to lots of readers too - so asking questions is good (especially for the (I suspect) quite large numbers that read this forum but never quite get around to asking questions).

       - Andy.


  • Sparkingchip:

    I have found 30 mA versions, that’s why if I cannot see a rating label I put the tester on them to see what happens and some fo work.


    As to what is behind a locked door, there’s only one way to find out.


    The Crabtree P60 current operated earth leakage circuit breaker that looks like yours in your photos in a grey/cream insulated enclosure could be obtained with or without overcurrent protection. It was rated at 60 Amps max.

    It was called a High Sensitivity Current Operated E.L.C.B. The 1975 Crabtree  catalogue states a sensitivity of 25mA. I have a version of it that has a label stating 30mA sensitivity.


    My version is the one with an electronic amplifying principle module. It is on the right and is brick shaped and coloured black No coil can be seen.


    Back in the mid/late 70s the unit without the overcurrent protection part cost £27.85 each. It was list number 13000/25.


    Z.


  • Try this one from 1940.

    8c36f5dd13efb7694dfb302207164cb6-original-20210425_170734.jpg