Problem is that even if those plumbers have heard of diversity, they probably think that it means that you have to genuflect at the start of a game or race. ?
I don't think that I would apply diversity to a normal basic fixed load shower. It can probably be set at half load or full load with two sets of heating elements. I would rate it at full load Amps. for cable sizing. The previously mentioned all singing all dancing electronic shower automatically adjusts the load current I believe, according to the incoming water temperature and the water temperature set by the user for comfort. So in that case things may be different in practice, but I would still chose a supply cable based on full load current.
Z.
AJJewsbury:Clipped direct includes cables installed on brick walls with or without capping covered in plaster
Indeed. On the other hand most shower cables run through a floor void at some point - that's method B - now what does a 6mm² look like?
- Andy.
Will 'cable installed in a ceiling' in section 7.2 of Apdx 4 also apply if there's no junction box, just the cable in the ceiling, that refers to RM A?
Farmboy:AJJewsbury:Clipped direct includes cables installed on brick walls with or without capping covered in plaster
Indeed. On the other hand most shower cables run through a floor void at some point - that's method B - now what does a 6mm² look like?
- Andy.
Will 'cable installed in a ceiling' in section 7.2 of Apdx 4 also apply if there's no junction box, just the cable in the ceiling, that refers to RM A?
I believe that the junction box heat concerns apply to heat created by a luminaire, such as a tungsten filament lamp. Sometimes a junction box was situated close to or by a hot luminaire.
Table 4D5 is for use with cables at 30 degrees C ambient temp. and conductor operating temp. of 70 degrees C. You could warm your hands on a winter's day at 70 degrees C. The old fashioned big brown circular junction boxes that I use won't be adversely affected by a warm environment or catch fire.
Z.
Zoomup:Farmboy:AJJewsbury:Clipped direct includes cables installed on brick walls with or without capping covered in plaster
Indeed. On the other hand most shower cables run through a floor void at some point - that's method B - now what does a 6mm² look like?
- Andy.
Will 'cable installed in a ceiling' in section 7.2 of Apdx 4 also apply if there's no junction box, just the cable in the ceiling, that refers to RM A?I believe that the junction box heat concerns apply to heat created by a luminaire, such as a tungsten filament lamp. Sometimes a junction box was situated close to or by a hot luminaire.
Table 4D5 is for use with cables at 30 degrees C ambient temp. and conductor operating temp. of 70 degrees C. You could warm your hands on a winter's day at 70 degrees C. The old fashioned big brown circular junction boxes that I use won't be adversely affected by a warm environment or catch fire.
Z.
Yes but if it's acknowledged that cables in a building void (such as in a ground floor floor void) are RM B, then should RM A be used for cables in ceiling/floor voids (such as between flats) even though there may be no JBs, just the cable in the ceiling void?
Farmboy:Zoomup:Farmboy:AJJewsbury:Clipped direct includes cables installed on brick walls with or without capping covered in plaster
Indeed. On the other hand most shower cables run through a floor void at some point - that's method B - now what does a 6mm² look like?
- Andy.
Will 'cable installed in a ceiling' in section 7.2 of Apdx 4 also apply if there's no junction box, just the cable in the ceiling, that refers to RM A?I believe that the junction box heat concerns apply to heat created by a luminaire, such as a tungsten filament lamp. Sometimes a junction box was situated close to or by a hot luminaire.
Table 4D5 is for use with cables at 30 degrees C ambient temp. and conductor operating temp. of 70 degrees C. You could warm your hands on a winter's day at 70 degrees C. The old fashioned big brown circular junction boxes that I use won't be adversely affected by a warm environment or catch fire.
Z.
Yes but if it's acknowledged that cables in a building void (such as in a ground floor floor void) are RM B, then should RM A be used for cables in ceiling/floor voids (such as between flats) even though there may be no JBs, just the cable in the ceiling void?
It seems to be an engineering judgement call based upon experience. I can't imagine a shower cable getting too hot and becoming damaged for a short shower use of say 10 minutes. J.B.s are not an issue here.
Z.