davezawadi (David Stone):
Thanks OM for pointing that out, Error on my part typing! I have corrected it.
That C2 you mention is ridiculous, it doesn't matter, except it is likely to trip with long use. I hope you did nothing!
Yep, I did nothing. But I think we have found a solution to "teenage girls" problem. ?
OlympusMons:
Farmboy and Dave, you both mention RM A in your posts when i think you mean RM C. RM A refers to cables in conduit in an insulated walls (and architraves & windowframes). I agree it should be RM C in most ceiling voids.
I did remedials on an EICR recently and the cable type on the schedule of test results was given for all circuits as "A", as was the reference method. I was searching everywhere for cables in an insulated wall, especially near the CU since all circuits were classed as RM A, could't find any insulation. It was the same situation as Dave has, 6mm T&E, 8.5KW shower on a 40A MCB. The inspector C2ed it and recommended putting a 32A mcb in instead, "over-sized over current protective device".
I was referring to section 7.2 in regs appendix 4, page 384, which suggests RM A for 'cables installed in a ceiling', due to possible rise in temperature in JBs . So what I was trying to determine was should a cable in a ceiling void be considered as RM A even when no JBs are present, as the cables could still be subjected to the raised temperature?
wallywombat:
In terms of power loss:
If my back-of-the-envelope sums are right, a 15m run of cable for a 45A shower will give 1.7% power losses for 6mm2 and 1% for 10mm2. The larger cable will cost an extra £10 approx, so will pay for itself after about 70 kWh of reduced losses, or 10,000 kWh of shower usage, or about 1000 hours of use. Not sure what that is in units of Teenage Daughters.
I get slightly more. The difference in resistance between the two cable sizes is 4.05 mΩ/m so 61 mΩ. Power = I²R = 123 W extra. For a 15 min shower, that is 1/8 x 1/4 = 1/32 kWh. At 16 p that is a ha'penny per shower, so pay back is after 2000 showers or about 2 years for a hygienic family of three.
Chris Pearson:wallywombat:
If my back-of-the-envelope sums are right, a 15m run of cable for a 45A shower will give 1.7% power losses for 6mm2 and 1% for 10mm2. The larger cable will cost an extra £10 approx, so will pay for itself after about 70 kWh of reduced losses, or 10,000 kWh of shower usage, or about 1000 hours of use. Not sure what that is in units of Teenage Daughters.I get slightly more. The difference in resistance between the two cable sizes is 4.05 mΩ/m so 61 mΩ. Power = I²R = 123 W extra. For a 15 min shower, that is 1/8 x 1/4 = 1/32 kWh. At 16 p that is a ha'penny per shower, so pay back is after 2000 showers or about 2 years for a hygienic family of three.
A nice warm cable near to water pipes in the loft will stop them freezing up. Like trace heating. It's an ill wind that blows nobody any good. Perhaps the shower cable should be tied to a cold water pipe for most of its run.