MHowell:
. . . Putting everything on one circuit creates another problem though as there was to be a device fitted to monitor total load at the meter and to throttle back the supply to the charger if it got close to the 100A max available but clearly I would not want the garage lights dimming too. . .
The charge rate is set by the car, not the charger or the installation. The charger you are talking about does have a connection to monitor the current drawn by your installation, but this is connected to the charger and used to negotiate a different charging current with the vehicle, based on the load being drawn from the DNO supply. The charger will be configured with the maximum available.
As others have said, several cables from the same supply point feeding your garage is not an issue. As Broadgage has pointed out, the issue is two DNO supplies into the same property.
Regards,
Alan.