Simon Barker:perspicacious:
This doesn't necessarily mean that the supply is capable of supporting 100A, just that the individual bits of equipment can. For example a cut-out may say "100A BS 1361", but that just means the maximum fuse it can support. It may well have an 80A fuse it.
What colour is the cut-out? Grey or black?
Regards
BODHas the anti-EV brigade taken over this forum?
There's no problem running an EV charger off an 80A supply. Or a 100A supply that can only supply 100A for short periods.
No disagreement there Simon but I think that in most domestic installations the addition of a charge point rated at 7Kw will push the MD over 60A (using standard load assessment). That being the case, the DNO must be notified PRIOR to installation. With load management, notification can be given to the DNO within 28 days AFTER the install. If you communicate with the DNO in this area, you will be lucky to get a response by next Christmas! Hence it is highly beneficial for contractors to fit load management when the just want to get the job done.
As MapJ has pointed out this only serves the individual property. Things may get tricky for DNOs as EV uptake increases. No doubt that is what the smarts and OCPP is all about.
Simon Barker:perspicacious:
This doesn't necessarily mean that the supply is capable of supporting 100A, just that the individual bits of equipment can. For example a cut-out may say "100A BS 1361", but that just means the maximum fuse it can support. It may well have an 80A fuse it.
What colour is the cut-out? Grey or black?
Regards
BODHas the anti-EV brigade taken over this forum?
There's no problem running an EV charger off an 80A supply. Or a 100A supply that can only supply 100A for short periods.
No disagreement there Simon but I think that in most domestic installations the addition of a charge point rated at 7Kw will push the MD over 60A (using standard load assessment). That being the case, the DNO must be notified PRIOR to installation. With load management, notification can be given to the DNO within 28 days AFTER the install. If you communicate with the DNO in this area, you will be lucky to get a response by next Christmas! Hence it is highly beneficial for contractors to fit load management when the just want to get the job done.
As MapJ has pointed out this only serves the individual property. Things may get tricky for DNOs as EV uptake increases. No doubt that is what the smarts and OCPP is all about.