There's no problem running an EV charger off an 80A supply. Or a 100A supply that can only supply 100A for short periods.
True. and not anti EV,
But...
someone will need to pay to upsize the transformer after there are more than perhaps the first 6-10 houses per phase of the substation that have EV commuters.
It will become vitally important to understand ADMD (and also DNO cable ratings - see pages 8-13 ) - this is not like adding electric showers that are each on for 15 mins at a time tops.
You may not realise that round here a typical housing estate 500KVA lump will feed ~ 200 single phase properties each with 100A fuse, and most built up areas will be similar. Out of town the pole pigs that feed a couple of farm houses may do better, as the smallest Tx they install these days are either 25kVA or 50KVA split phase, even if only for a couple of properties.
M.
Has the anti-EV brigade taken over this forum?
There's no problem running an EV charger off an 80A supply. Or a 100A supply that can only supply 100A for short periods.
True. and not anti EV,
But...
someone will need to pay to upsize the transformer after there are more than perhaps the first 6-10 houses per phase of the substation that have EV commuters.
It will become vitally important to understand ADMD (and also DNO cable ratings - see pages 8-13 ) - this is not like adding electric showers that are each on for 15 mins at a time tops.
You may not realise that round here a typical housing estate 500KVA lump will feed ~ 200 single phase properties each with 100A fuse, and most built up areas will be similar. Out of town the pole pigs that feed a couple of farm houses may do better, as the smallest Tx they install these days are either 25kVA or 50KVA split phase, even if only for a couple of properties.
M.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site