Unfused spur.

Hello All,


Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?


Z.
  • AJJewsbury:
    The 1.5mm2 6242Y is no longer than 300mm and runs through a brick wall. It starts from a deeply sunk double metal box and terminates at a surface mounted all insulated 13 Amp. I.P. 64 rated single 13 Amp socket. Any physical damage is very unlikely.

    It's not just about physical damage - faults can occur from many causes. I'm sure we've all come across back boxes where a wire has come loose and touched something it shouldn't or been nicked by one of the faceplate fixing screws (possibly after Mr DIYer has been loosening faceplates to redecorate or otherwise messing with things).


     


    The metal box of the double socket in the house, on the ring,  is earthed by 2 X 1.5 mm2 C.P.C.s. The outdoor single socket is all insulated. So we have a very well earthed metal box in the house. Then the 300mm long  1.5mm2 6242Y cable runs through a brick wall to an all insulated outside socket.


    Z.


  • davezawadi (David Stone):

    Don't worry Zoomup, it wasn't really you! The case we are considering is as you have probably noticed is really quite complicated, and therefore not in the "normal" range of installation designs. If you had used a bit of 2.5mm, no one would have said a word, but some quite important stuff would not have got an airing here. The discussion has covered two different scenarios, the TT one where the Earth fault current is limited to a low value by Re, and the TN-S one where the fault current is limited by the source impedance and the wiring resistance. You have now told us that each leg of the ring is probably about 15 metres, and so we can calculate the maximum fault current. We also know the ability of a 1mm cable to withstand this current for the time necessary to trip the MCB, and can therefore decide that the installation is satisfactory.


    Kind regards

    David


    Thanks. Would the swift operation of the R.C.D. limit the time the fault current flows, on a L to E fault, thus reducing the heating effect due to energy let through on the 1.0mm2 C.P.C? The R.C.D. should open within 2 cycles shouldn't it?


    Z.


  • davezawadi (David Stone):

    No Andy, it is not that you must assume the energy let through is the maximum, it cannot be unless the fault current is very high. The B32 for instance characteristics in the Regs shows a vertical line on the graph at 600A fault current, which according to the graph is between 10ms and 5 seconds. This is the instantaneous region, and the worst case is your energy let through. You are assuming the worst case can occur anywhere in the characteristic, but this is not the case. You will see the note on the graph, which says the worst case is at the high end of fault current. You do not and cannot have this, so the let-through must be less. Instantaneous operation is usually considered 10ms, not you see an unreasonably quick figure. Therefore the energy let through is I2t Watts, so the current is the important factor.


    I read the graph at 160A down to 100ms - but that's an aside. I agree the energy let-though will be less than 18,000A²s, but my point is that in order to show compliance we need to actually quantify how much less - specifically that it'll be no higher than 13,225 A²s to suit 1mm² Cu in a PVC cable. I still think we don't have the MCB data to do that.


    If from Z's latest posting we can deduce that the fault current will be below 575A (but above 250mA) then we can use the 40ms disconnection time of the 30mA RCD and that should be fine.


       - Andy.


  • Would the swift operation of the R.C.D. limit the time the fault current flows, on a L to E fault, thus reducing the heating effect due to energy let through on the 1.0mm2 C.P.C? The R.C.D. should open within 2 cycles shouldn't it?

    The maths is easy enough - the best we're guaranteed for a 30mA RCD is that it opens within 40ms at significant fault currents -  5x IΔn or above (or 250mA for some makes) - so you can calculate the energy let-though as just I²t - so for say 600A fault and 0.04s we'd have 600² x 0.04 = 14,400A²s. Then compare that with the withstand of the cable - k²S² - k for a PVC cable is 115 and so for a 1mm² conductor it comes out at 13,225 A²s.


       - Andy.
  • That constant of 115 is not of course related to the ultimate failure temperature  of the copper core, or anything like it,  just that it has got hot enough to begin to damage the PVC on either side of it, and repeated faults at this level may lead to core to core  shorts within the cable too.


    If you are only worried about failure of the CPC itself (as  in melting metal), then it needs to go up by a factor of about 20. By which time the insulation has well and truly bought it.

    Mike.
  • I have now read you many times on this subject Andy on various posts. The point is that you are not understanding this at all. Let's look at the TN conditions again if you like.  In the most simplistic terms, say the CPC was a fuse, what time would be required to cause it to fail at the available fault current? Let's look at the available fault current first, what is it? At the DB, Z says it is about 890A. We have about 15 m doubled in the ring, so 7.5m The resistance of this is about 135 mOhms. The mains supply impedance is 0.26 Ohms by calculation. Therefore the L-N PSCC is 230/0.397 = 578A (About Mikes figure). At this current the breaker opens in less than 10ms, giving a maximum I²t of 3341 A²s. What is the problem now?  It is even lower for a L-E fault because the Earth conductor has higher resistance. This is pretty simple electrical design stuff. You are imagining something which is not correct or possible. Z is perfectly safe. In this case, we will not even get to 115°C, the design criterion for multiple damage-free faults, which strictly speaking is not mandated by BS7671. Now the TT version, the fault current must pass through the Re, so is very much smaller, the RCD is subjected to a very small I²t, as is the 1mm conductor.


    (Joke) Here endeth the first lesson!
  • At this current the breaker opens in less than 10ms

    Where is that written? AFAIK BS 7671 doesn't say that and BS EN 60898 doesn't say that. I know of a rule of thumb that that the an MCB will generally open in between 0.1s and 0.01s but that's not the same thing at all.


    BTW k=115 has nothing to do with 115°C.


       - Andy.
  • I am unclear about the energy let-through subject. I squared t, or A squared t. (Amp2 seconds).


    I understand current and I understand time. Where did the current squared originate? ( I do know the origin of I squared R if that is similar).


    Also, are the values of current R.M.S. values? Which would give a heating effect the same as if the values used were D.C?


    As the value of Voltage changes over a cycle or two, will the energy let through value  alter as well, rather than being a fixed "packet" of energy? Or are we taking an average value of energy let-through over a period of time?


    I can not see us using instantaneous values for an event that takes place over a period of time.




    Thanks,


    Z.


  • I am unclear about the energy let-through subject. I squared t, or A squared t. (Amp2 seconds).


    I understand current and I understand time. Where did the current squared originate?



    I suspect you are not alone, the choice of units is not the most descriptive.  Really it is a measure of the total energy dissipated in  every small resistance in the fault loop, in the time between start of fault, and the disconnection.  At the risk of a long post, and not one for those short of sleep, it may help to play some algebra games.

    If need be print this out and take your time to digest it. (There is no exam at the end, except safe designs !)


    V*I = watts. (1)  (by definition) 

    V*I*t = joules (2)  (heat energy)

    V= I*R           (3) (Mr Ohm)

    so I*R*I*t = joules (merging statements 2 and 3)

    regrouping


    I*I*t*R = Joules

    divide both sides by R, this remains a true statement

    I2t = joules/ohms (5)

      Ta-da really these units are telling you that if you have say a switch contact of so many milliohms in series with a fuse of that let-through, it will be heated by that many joules per ohm  during the blowing time. If you know the contact heat capacity (so many degrees rise per so many joules of heat per certain mass or volume to be heated - watch you are using figures where the base  units are the same), you can then deduce a temperature rise, and decide if it will be damaged or not.


    Take the example of a simple copper wire 1mm2 in cross-section, and 1m long.

    total resistance call it 16 milliohms per metre of length (or 19 if it is hot)

    Total volume 1000mm3  

    total mass

    m=9 grams per metre of length

    (it is 9 tonnes  per cubic metre, but rescaled... )

    heat capacity per unit mass (S or Q in some texts), rescaled gives ~

    S=  0.38 joules will raise one gram by 1 degree C   (in vacuum with no heat escape allowed)

    temperature rise is more with more electrical power, but reduced by more mass of stuff to heat or higher heat capacity


    dT=I2R*t/(S*m)          (6)


    you can think of dT= difference in temperature


    So for an example say a 100 degree temperature difference between before and after


    100=I2R*t/(S*m)       (7)


    re order to get


    I2t=(S*m*dT)/R    (s)


    = (0.38*9*100)/0.016

    (note the per metre of length cancel as there is one on top one below.. )


     ~22 000 joules per ohm

    or 22,000 amps2 seconds will give a 100 degree rise in 1mm2 copper cable.


    for a 1000 degree rise, more like what it would take for copper to melt


    more like 220,000 amps2 seconds would be needed.


    In reality there is always some cooling, so these figures will not quite match tabulated ones from real experiments, the faster it blows the less time there is for heat to escape, the better this approximation fits.

    But it shows the technique.


    Come back if you need walking through it in finer steps.

    note I have broken my own rule of not doing algebra live on the forum. There may be errors, if so, let me know, I'll fix them to avoid misleading / confusing others.


    Mike.







  • mapj1:
    I am unclear about the energy let-through subject. I squared t, or A squared t. (Amp2 seconds).


    I understand current and I understand time. Where did the current squared originate?



    I suspect you are not alone, the choice of units is not the most descriptive.  Really it is a measure of the total energy dissipated in  every small resistance in the fault loop, in the time between start of fault, and the disconnection.  At the risk of a long post, and not one for those short of sleep, it may help to play some algebra games.

    If need be print this out and take your time to digest it. (There is no exam at the end, except safe designs !)


    V*I = watts. (1)  (by definition) 

    V*I*t = joules (2)  (heat energy)

    V= I*R           (3) (Mr Ohm)

    so I*R*I*t = joules (merging statements 2 and 3)

    regrouping


    I*I*t*R = Joules

    divide both sides by R, this remains a true statement

    I2t = joules/ohms (5)

      Ta-da really these units are telling you that if you have say a switch contact of so many milliohms in series with a fuse of that let-through, it will be heated by that many joules per ohm  during the blowing time. If you know the contact heat capacity (so many degrees rise per so many joules of heat per certain mass or volume to be heated - watch you are using figures where the base  units are the same), you can then deduce a temperature rise, and decide if it will be damaged or not.


    Take the example of a simple copper wire 1mm2 in cross-section, and 1m long.

    total resistance call it 16 milliohms per metre of length (or 19 if it is hot)

    Total volume 1000mm3  

    total mass

    m=9 grams per metre of length

    (it is 9 tonnes  per cubic metre, but rescaled... )

    heat capacity per unit mass (S or Q in some texts), rescaled gives ~

    S=  0.38 joules will raise one gram by 1 degree C   (in vacuum with no heat escape allowed)

    temperature rise is more with more electrical power, but reduced by more mass of stuff to heat or higher heat capacity


    dT=I2R*t/(S*m)          (6)


    you can think of dT= difference in temperature


    So for an example say a 100 degree temperature difference between before and after


    100=I2R*t/(S*m)       (7)


    re order to get


    I2t=(S*m*dT)/R    (s)


    = (0.38*9*100)/0.016

    (note the per metre of length cancel as there is one on top one below.. )


     ~22 000 joules per ohm

    or 22,000 amps2 seconds will give a 100 degree rise in 1mm2 copper cable.


    for a 1000 degree rise, more like what it would take for copper to melt


    more like 220,000 amps2 seconds would be needed.


    In reality there is always some cooling, so these figures will not quite match tabulated ones from real experiments, the faster it blows the less time there is for heat to escape, the better this approximation fits.

    But it shows the technique.


    Come back if you need walking through it in finer steps.



    Mike.







     


    Wow and thanks Mike. Thanks very much. I have never had it explained in the clear understandable terms that you have used. I am off to work now but will re-read your post later and retain it for future reference.