but as this is an unfused spur that doesn't really help for faults before the socket.
- Andy.
The 1.5mm2 6242Y is no longer than 300mm and runs through a brick wall. It starts from a deeply sunk double metal box and terminates at a surface mounted all insulated 13 Amp. I.P. 64 rated single 13 Amp socket. Any physical damage is very unlikely.
Z.
davezawadi (David Stone):
I was just reading the thread again and it is TT. The Earth fault current is therefore not a consideration unless there are metal service pipes and other properties which are TN, which seems very unlikely. I would like the measured values though!
The P.S.C.C. at the distribution board is approx. 0.89 kA L to N. I have no L to E reading as my tester is limited to 50 Ohms max. The physical condition of the earth electrode, well the top of it anyway, was inspected along with the main earthing conductor. The installation dates back to the 90s. Both R.C.D.s of the split load board were tested and operated at 29mS @ 5 X I delta n.
Z.
The 1.5mm2 6242Y is no longer than 300mm and runs through a brick wall. It starts from a deeply sunk double metal box and terminates at a surface mounted all insulated 13 Amp. I.P. 64 rated single 13 Amp socket. Any physical damage is very unlikely.
The energy let through you are quoting is at the DB with 6kA PSCC (or 3kA) .... The other points to consider are the PSCC at the point the 1.0 Earth conductor joins, which will not be 6kA or even 3kA, it might be as high as 575A if the ring is short and the DB PSSC high. The by the book calculation is not a theoretical possible maximum value, it is an actual value.