Unfused spur.

Hello All,


Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?


Z.
  • Thanks, Andy!   The only version of 60898 I'd found was an IS/IEC, i.e. Indian standard, from 2002, with appendices just A-L.  I don't have the BS-EN.  So I see it's more detailed in another version. Still, this Energy limiting class 1 looks like the old-style lack of requirement. 

  • The BEAMA "Guide to Low Voltage Circuit-Breakers Standards" June 2015 document reproduces some of the BS EN 60898 let through class values; they appear to be the same as the values Andy posted for type B class 3, but have slightly lower value let-throughs now for type C class 3:  3/4.5/6/10 kA Icn has breaking capacity of  17/28/40/80 kA for <= 16A and 20/37/52/100 for 20-32A.


    (It doesn't  give figures for class 2).