This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Heat Tracing Questions

1. Why the heat tracing cables draw more current during starting at start up temperature?

2. How self regulated tracing cables are inherently safe and can be used in hazardous area?

3. How the Maximum circuit length is determined according to the breaker type? What is the equation used here? (see the picture below)
e67a1e17174e1cfe703103d0d31160e2-huge-maximum-circuit-lenght.png
Parents
  • 1. In most conductors, the resistance goes up with temperature.  So the current is greatest when cold, and drops as the cable warms up.

    2. Because of 1.  The cable is naturally self-limiting - as it gets hotter, the current drops, which prevents any thermal runaway.

    3. Who knows?  Ask the manufacturer.  Roughly speaking, the current is proportional to the cable length.  But the breaker values there only vaguely approximate to that.
Reply
  • 1. In most conductors, the resistance goes up with temperature.  So the current is greatest when cold, and drops as the cable warms up.

    2. Because of 1.  The cable is naturally self-limiting - as it gets hotter, the current drops, which prevents any thermal runaway.

    3. Who knows?  Ask the manufacturer.  Roughly speaking, the current is proportional to the cable length.  But the breaker values there only vaguely approximate to that.
Children
No Data