Heat Tracing Questions

1. Why the heat tracing cables draw more current during starting at start up temperature?

2. How self regulated tracing cables are inherently safe and can be used in hazardous area?

3. How the Maximum circuit length is determined according to the breaker type? What is the equation used here? (see the picture below)
e67a1e17174e1cfe703103d0d31160e2-huge-maximum-circuit-lenght.png
Parents
  • The safety thing is the absence of  external wiring to a thermostat with possibly arcing contacts - there are no moving parts, so no worry about vapours and gas ignition.


    The wire alloys and insulation between them are chosen so that there is a sharp rise in resistance with temperature - far more than with a normal metal, where resistance rises with absolute temperature (so freezing is 273 degrees, and boiling is 373 -  a change in resistance of a mere 35% over 100degree change is not enough.)


    The kind where both L and E go in at the same end are easier to deal with, as  it is more like a set of festoon lights, with lots of little variable resistance heaters strung like the rungs of a ladder between low resistance wires with supply between them.  These can be made to length more or less as required.


    The kind with one wire core and L and N at opposite ends are fixed resistance must not be shortened without adjusting the supply voltage so the number of volts per metre is constant.


    However in either case there are now a couple of considerations when sizing the breakers.

    1 temperature matters - no good if the current is so high the breaker fires on a cold morning. (!!!)

    2 the wire has resistance - but if the cable is cut and shorted out near the far end, you need enough extra current to flow, (even on a hot high resistance sort of day), that the breaker will trip correctly.

    The practical upshot is that there is both a max length and  breaker rating limit for the breaker to work if there is a  fault, and another breaking limit for a given length for it not to fire on cold days. the table tries to indicate a range of sensible cable lengths for a given breaker rating.

    In general short runs of trace cable are easy, and long ones are better sub-divided or fed from the centre outwards.

    Mike

Reply
  • The safety thing is the absence of  external wiring to a thermostat with possibly arcing contacts - there are no moving parts, so no worry about vapours and gas ignition.


    The wire alloys and insulation between them are chosen so that there is a sharp rise in resistance with temperature - far more than with a normal metal, where resistance rises with absolute temperature (so freezing is 273 degrees, and boiling is 373 -  a change in resistance of a mere 35% over 100degree change is not enough.)


    The kind where both L and E go in at the same end are easier to deal with, as  it is more like a set of festoon lights, with lots of little variable resistance heaters strung like the rungs of a ladder between low resistance wires with supply between them.  These can be made to length more or less as required.


    The kind with one wire core and L and N at opposite ends are fixed resistance must not be shortened without adjusting the supply voltage so the number of volts per metre is constant.


    However in either case there are now a couple of considerations when sizing the breakers.

    1 temperature matters - no good if the current is so high the breaker fires on a cold morning. (!!!)

    2 the wire has resistance - but if the cable is cut and shorted out near the far end, you need enough extra current to flow, (even on a hot high resistance sort of day), that the breaker will trip correctly.

    The practical upshot is that there is both a max length and  breaker rating limit for the breaker to work if there is a  fault, and another breaking limit for a given length for it not to fire on cold days. the table tries to indicate a range of sensible cable lengths for a given breaker rating.

    In general short runs of trace cable are easy, and long ones are better sub-divided or fed from the centre outwards.

    Mike