AJJewsbury:
That's generally only true for TT systems - in TN it's usual for overcurrent devices (MCBs, MCCBs, fuses) to provide earth fault protection too.
- Andy.
Do you meant to say that in TN systems, the earth fault current is sufficient to operate the generic breakers?
Nick Parker:AJJewsbury:
That's generally only true for TT systems - in TN it's usual for overcurrent devices (MCBs, MCCBs, fuses) to provide earth fault protection too.
- Andy.Do you meant to say that in TN systems, the earth fault current is sufficient to operate the generic breakers?
It certainly can be, especially in TN-C-S situations. Just draw the circuit and see the earth fault loop path. In B.S. 7671 the earth fault current is defined as resulting from a fault of negligible impedance. The cables to and from the earth fault point will in practice have an impedance of course.
411.4 onwards.
Z.