End of line fault

Why calculate end of line fault current? 

Is it for verifying that thermal stress could be withstood by the cable before the breaker gets tripped?

Is it to verify that breaker to be tripped in a certain time (1s or 5s) for the fault current magnitude at the end of line?


I have a colleague who says, only phase to phase faults to be calculated at the end of line.  I ask why not the phase to earth or Phase to neutral for which his reply is, Generic MCCB or MCBs would not work for earth faults.


The Generic MCCBs would work for earth fault provided the fault magnitude is greater than the magnetic trip threshold (Im). Now what if the Phase to earth fault's magnitude is lesser than the Magnetic Pick up. Should RCD be provided?


I think it is the job of the designer to find the minimum fault current at the end of the line (whether it is P-P or P-N or P-E) and select the breaker which guarantees trip the minimum fault current
Parents
  • Yes, both of the "worst cases" need to be considered.

    Close to the OCPD the fault current must be determined and shown to be within the breaking capacity of the MCCB or other protective device. This should be whichever is HIGHEST out of phase/earth, phase/neutral, or phase/phase.

    It would in most cases be prudent to allow for changes to the supply arrangements that may increase the fault current. For example load growth that requires a larger transformer, or multiple transformers. Or the replacement of local generation by a grid connection.


    At the distant end of the circuit, the fault current must be determined and shown to be sufficient to operate the MCCB or other protective device in the desired time. This should be the LOWEST of phase/earth, phase/neutral, or phase/phase. It may be possible to ignore the phase/earth scenario if reliance is placed is placed upon an RCD or upon earth fault protection incorporated in the MCCB for such events.
Reply
  • Yes, both of the "worst cases" need to be considered.

    Close to the OCPD the fault current must be determined and shown to be within the breaking capacity of the MCCB or other protective device. This should be whichever is HIGHEST out of phase/earth, phase/neutral, or phase/phase.

    It would in most cases be prudent to allow for changes to the supply arrangements that may increase the fault current. For example load growth that requires a larger transformer, or multiple transformers. Or the replacement of local generation by a grid connection.


    At the distant end of the circuit, the fault current must be determined and shown to be sufficient to operate the MCCB or other protective device in the desired time. This should be the LOWEST of phase/earth, phase/neutral, or phase/phase. It may be possible to ignore the phase/earth scenario if reliance is placed is placed upon an RCD or upon earth fault protection incorporated in the MCCB for such events.