Re Cable choice - what options would you personally go for?Main cable runs to power sockets and/or isolators around perimeter on tray and clipped direct, all above 1m from ground - NYY? SWA?
Secondary cable runs from Isolator (1m above ground) to Element (30cm above ground) - CY? NYY? SWA?
Cheers!
Very difficult to say - I'm not able to see the overall situation remember.
If the robustness of SWA isn't necessarily needed, I might consider BS 8436 types (which goes under various brandnames, but often have "shield" in the name) - much easier to dress and gland off than SWA, but you still get some decent protection from shock if the cable is damaged (unlike all-insulated types), easy to get a decent IP rating using simple stuffing glands, and you get some reasonable screening thrown in too. But that's just thought to add to your list - rather than a recommendation.
If the heaters are similar to domestic immersion heaters, there's likely to be a requirement for heat resisting cabling - so heat resisting (HOFR) flex would be my first thought - but again that can't be a recommendation. Hopefully the heater's installation's instructions give you a clue to what's actually required. Likewise the heater's boss might constrain your choice (is it fitted with a 20mm threaded inlet or a cord grip that'll only accept flex for instance?)
- Andy.
mapj1:
Mind you the one time H07 and similar non shielded 'soft' flex are used (and used by the mile) are the film industry, and events like pop festivals and concerts, where it gets a real beating, being run over and knotted and quite often pulled about with fair robustness during installation as well - and it is in fact surprisingly robust. But yes, you do expect to see ferrules, and the right sort of cord grips at each end.
You may well want something of that sort at least for the last hop from isolator to immersion heater. But I'd certainly agree, it is not common for fixed wiring, where something with a harder jacket and less finely stranded cores is expected.
Mike.
Cheers Mike.
What options would you personally go for?
Cable choice 1 - For main cable runs to power sockets and/or isolators around perimeter run via tray and/or clipped direct, all above 1m from ground - NYY? SWA? Something else?
Cable choice 2 - For secondary cable runs from Isolator (1m above ground) to Immersion Elements (30cm above ground) - CY? NYY? SWA? Something else?
AJJewsbury:Was wondering if H07RN-F would also be suitable option?
Flex isn't often used for fixed wiring - partly because it's more expensive and harder to dress neatly, but also because the finely stranded conductors may need special preparation (e.g. ferrules) for use in some types of terminals. It's more usual to use a rigid conductor system for the fixed wiring and then transition to flex for the final span to the appliance where flexibility or heat resistance is required. Immersion heater normally require heat resisting flex for example.
Cheers Andy.
The H07RN-F I'm looking at has rigid conductors:
https://www.superlecdirect.com/cables-and-accessories-c1/h07rnf-flex-mains-and-control-cables-en6033212-s185/
I see that NYY is compatible with 20/25 cable glands though, so may be a neater and more IP rated job all round?
https://www.superlecdirect.com/cables-and-accessories-c1/iec605021-vde-0276603-nyyj-cable-s11/
The H07RN-F I'm looking at has rigid conductors:
Nano Brewery:The H07RN-F I'm looking at has rigid conductors:
https://www.superlecdirect.com/cables-and-accessories-c1/h07rnf-flex-mains-and-control-cables-en6033212-s185/
So maybe SY or SWA for this?