Ze readings on a TT system

Former Community Member
Former Community Member
Hi

I have a TT system on a farm where the ze readings are

L1 = >2000

L2 = 1.43

L3 = 1.41

readings took at the henley blocks directly from the meter. There's voltage on L1 and all the 3 phase equipment runs OK.

can anyone tell me why I'm getting this high reading.


Many thanks

BR
Parents



  • There is something about zeroing the meter before carrying out a loop test in the instructions. Also the meter may not work if overheated due to being overused.


     I am currently reading through the user's manual. 

    Fluke1651_User.pdf (tlc-direct.co.uk)


    Z.
Reply



  • There is something about zeroing the meter before carrying out a loop test in the instructions. Also the meter may not work if overheated due to being overused.


     I am currently reading through the user's manual. 

    Fluke1651_User.pdf (tlc-direct.co.uk)