Weirdbeard:
Hi BR, welcome to the forum!
1.4 (ohms?) seems a bit low for L2 and 3, could you describe the situation in more detail or if possible a few photos would really help.
:)
Hello Weirdbeard,
I have seen steel framed farm buildings with many feet buried in the soil where the steel is used as an earth electrode. Multiple electrodes.
Z.
BR:
Hi
I've got 6 rods in the ground in 3 sets of 2 screwed together plus the ground is very wet at the moment. I've changed a sub board and found this problem when testing. The zs readings at the board incomer are L1 >2000
L2 1.78, L3 1.84, simular to what's at the main.
The final circuits are mainly 3 phase sockets with a couple of lighting circuits. The socket below the board has the same issue but all the others have balanced zs ( 2.0 ohm approx) values across all 3 phases just to confuse me even more.
Thanks again
BR
Corrosion at a C.P.C. connection/joint then. Do any L1 cables run in steel conduit or trunking.
Z.