2.5 mm SWA out of the back of a socket into a small consumer unit in the shed with a 16 amp MCB in it to feed a 2.5mm radial circuit within the shed for sockets and a switched 3 amp fused connection unit to supply the shed lights.
Done and dusted.Hi Andy, how do you connect an SWA out of the back of a domestic socket and it be available for future inspection?
if you look at some of the You Tube electricians, the current trend would suggest the armour's cut off at the supply socket, so just the insulated copper cores in their jacket enter the box, with the armour earthed at the load end.