Sparkingchip:
2.5 mm SWA out of the back of a socket into a small consumer unit in the shed with a 16 amp MCB in it to feed a 2.5mm radial circuit within the shed for sockets and a switched 3 amp fused connection unit to supply the shed lights.
Done and dusted.
Hi Andy, how do you connect an SWA out of the back of a domestic socket and it be available for future inspection?
Weirdbeard:Sparkingchip:
2.5 mm SWA out of the back of a socket into a small consumer unit in the shed with a 16 amp MCB in it to feed a 2.5mm radial circuit within the shed for sockets and a switched 3 amp fused connection unit to supply the shed lights.
Done and dusted.Hi Andy, how do you connect an SWA out of the back of a domestic socket and it be available for future inspection?
Might have to be wired through a box on the external wall as getting a gland into the back of the socket will be a challenge, though not impossible.
PG:
Cables (2 x 2.5 T&E) out of the back of the indoor twin 35mm deep socket box, through the wall, into a plastic conduit box and 25mm pvc conduit dropped 18" underground to shed position.
Concerning the socket box: is the intention to joint one leg of the ring in there, or go back to the previous socket in the ring?
Is PVC conduit suitable for use as an underground duct? How will water be excluded?
I do not have any problem whatsoever electrically with extending the ring, and Mike's upside-down lollipop is just as good; but what troubles me a little is whether there will be adequate protection from external influences.