mapj1:
.
Another (but highly non standard) approach, and one that may therefore have a few folk sucking their teeth, could be a 4mm unfused spur from the 2.5mm ring- again the loading on the rest of the ring is the same as if you had extended the ring, but the outdoors can be isolated more readily if there is a problem.
M.
As a rule of thumb for rings, unfused spurs should not exceed 1/8 the cable length from the spur to the furthest point in the ring.
The unfused spur cannot be an extension onto a ring if the rule of thumb is complied with.
Chris Pearson:PG:
Cables (2 x 2.5 T&E) out of the back of the indoor twin 35mm deep socket box, through the wall, into a plastic conduit box and 25mm pvc conduit dropped 18" underground to shed position.Concerning the socket box: is the intention to joint one leg of the ring in there, or go back to the previous socket in the ring?
Is PVC conduit suitable for use as an underground duct? How will water be excluded?
I do not have any problem whatsoever electrically with extending the ring, and Mike's upside-down lollipop is just as good; but what troubles me a little is whether there will be adequate protection from external influences.
The ring is joined in the socket box
I think PVC conduit will be a reasonable water proof duct. Installed without joints so water ingress shouldn't be a problem. I'll add some sealant between the conduit box and the brick wall.
Weirdbeard:Sparkingchip:
2.5 mm SWA out of the back of a socket into a small consumer unit in the shed with a 16 amp MCB in it to feed a 2.5mm radial circuit within the shed for sockets and a switched 3 amp fused connection unit to supply the shed lights.
Done and dusted.Hi Andy, how do you connect an SWA out of the back of a domestic socket and it be available for future inspection?
if you look at some of the You Tube electricians, the current trend would suggest the armour's cut off at the supply socket, so just the insulated copper cores in their jacket enter the box, with the armour earthed at the load end.
Hello all,
I have tried to research my question but find confusing and predominantly old replies to similar problems. To be sure on all counts I thought I would ask again.
I am a joiner asked to construct a shed base, and assemble bought shed. The main house has an interior double 13amp socket close to an outside wall. The idea is to take a spur off that socket with 1.5mm armoured cable, run it through the outside wall and onwards under decking and through a slit trench to a garden shed. Distance to shed between 10-15 metres. Ideally then to provide a light in the shed and a couple of 13amp sockets. More ideally an all weather external socket outside the shed too.
Note the existing consumer unit is on the wrong side of the house.
So questions:
Can such a spur be safely taken off that double socket ?
If yes, can the double socket be left working or does the spur replace it (blanked off)?
Is 1.5mm cable enough or 2.5mm better?
Does (can?) that spur need any form of extra inline fusing (RCD?) or will the house one suffice?
Can a spur happily deal with a light and 2/3 plugs. If so is it best run off a fused junction box as it enters the shed end?
Any advice much appreciated.
Cheers
John