Cable current rating advice

Former Community Member
Former Community Member
Hi all, I would like to verify something with respect to current carrying capacity of cable. Specifically vehicle single core DC circuits.


Looking at 16mm wire not worrying about voltage drop. manufacturers are ratting this at 110A and on a forum I subscribe to people have been advised 125A is ok.


The cable is rated at 70 deg as shown on the suppliers site linked below.

16mm supplier


Am I wright that this comes under 

Table 4D1A


Single-core 70°C Thermoplastic Insulated Cables, Non-Armoured, with or without Sheath


Reference Method C (clipped direct) This will be between battery to battery not in any conduit or insulation


So is rated as 87A


I would be interested in your advice as it has been several years since I used these tables
Parents
  • edit :

    replying to Steve above, not Roger ,

    Note that  100A , 50 degree rise case may be just about OK in a 70c engine bay type environment, as the core is now at 120C, but it is not good for the cable.

    Of course in vehicles a lot of the loads are different durations - motors for windows and so on, are not not really the same as windscreen wipers, as the latter may be on all day ?.

    At the other extreme we have the kilowatt audio soundblaster that luckily only draws lots of amps when the drums go bang, and has an average of perhaps 10% of the peak, but the enthusiasts pay for cables based on the peak current.


    I'd be tempted, especially near batteries, perhaps with long charging periods, to double up (so twice the copper, half the rating) if there is any doubt. But it is not simple, and short of instrumenting the wire loom and then running it, the answer is really quite uncertain.

    As an aside I have worked on things where we embed temperature indicating labels, so we can tell when stuff comes back under warranty if it has been abused. These have tended to show that bundled wiring runs cooler than the theory predicts, and on the other hand heatsinks do not always work as well as expected...

    mike.
Reply
  • edit :

    replying to Steve above, not Roger ,

    Note that  100A , 50 degree rise case may be just about OK in a 70c engine bay type environment, as the core is now at 120C, but it is not good for the cable.

    Of course in vehicles a lot of the loads are different durations - motors for windows and so on, are not not really the same as windscreen wipers, as the latter may be on all day ?.

    At the other extreme we have the kilowatt audio soundblaster that luckily only draws lots of amps when the drums go bang, and has an average of perhaps 10% of the peak, but the enthusiasts pay for cables based on the peak current.


    I'd be tempted, especially near batteries, perhaps with long charging periods, to double up (so twice the copper, half the rating) if there is any doubt. But it is not simple, and short of instrumenting the wire loom and then running it, the answer is really quite uncertain.

    As an aside I have worked on things where we embed temperature indicating labels, so we can tell when stuff comes back under warranty if it has been abused. These have tended to show that bundled wiring runs cooler than the theory predicts, and on the other hand heatsinks do not always work as well as expected...

    mike.