Out out voltage of 3 phase inverter

I’m trying to understand if we have a three phase motor 50/60hz what would we set the voltage at for the inverter?  If 50hz I can see it being 415 here in the uk but say if we was running the motor at 60hz can we up the voltage to say 480v? 


thanks guys
Parents
  • i presume the
    22B-E012x104   7kW unit

    or maybe the
    22B-E9P9x104     5.5kW unit


    Be aware that the output is not a sine wave, anything like, so the normal RMS voltage and current thing  will not read on most meters.

    really the incoming 3 phase is rectified to give a DC bus, and then fast switching transistors connect and disconnect with varying mark to space ratio, to give an average force on the coils equivalent, roughly, to a sine wave. (long bursts on and short time off to mimic the peak of the sine, and long off, short on to mimic the near zero part.)

    The chopping frequency is sometimes called carrier, after the radio analogy of modulation.

Reply
  • i presume the
    22B-E012x104   7kW unit

    or maybe the
    22B-E9P9x104     5.5kW unit


    Be aware that the output is not a sine wave, anything like, so the normal RMS voltage and current thing  will not read on most meters.

    really the incoming 3 phase is rectified to give a DC bus, and then fast switching transistors connect and disconnect with varying mark to space ratio, to give an average force on the coils equivalent, roughly, to a sine wave. (long bursts on and short time off to mimic the peak of the sine, and long off, short on to mimic the near zero part.)

    The chopping frequency is sometimes called carrier, after the radio analogy of modulation.