Out out voltage of 3 phase inverter

I’m trying to understand if we have a three phase motor 50/60hz what would we set the voltage at for the inverter?  If 50hz I can see it being 415 here in the uk but say if we was running the motor at 60hz can we up the voltage to say 480v? 


thanks guys
Parents
  • if you wire it as a delta, yes.

    Being a nervous fella, if I could I'd start with the shaft load reduced or off, and a lower voltage, just to check it behaves.

    what is it turning?

    M.
Reply
  • if you wire it as a delta, yes.

    Being a nervous fella, if I could I'd start with the shaft load reduced or off, and a lower voltage, just to check it behaves.

    what is it turning?

    M.