This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Safe Disconnection to Undertake Work.

Scene. An old farm building now used as a double glazing frame maker's workshop.


The supply comes from an old shed about 40 metres away, where the meter is. The old shed has some 70s/80s rusty M.E.M. isolators that feed several S.W.A. cables that exist the shed in many directions underground. I suspect that one feeds the main farmhouse, another a rented cottage and the others various farm buildings. There is no clear labelling of the isolators.


What is the best way to locate the frame maker's  building supply where I have to work?


Somewhere I have a circuit i/d set, if I can find it, but that will need access to the live parts and I do not wish to turn off the wrong isolator.


Z.


Parents
  • Are all the SWA cables the same diameter and make ? if you can see the jackets you may be able to reduce the scope for error.

    If you are brave you could try injecting a modest current onto the armour - ideally you'd need to lift the earth at the load end and that may not be possible or safe.

    However,  assuming the armour is the CPC, or at least part of the CPC, then  pulling an L-E fault current of a few amps ought to allow the correct SWA to be isolated with nothing more than  a clamp meter over the jacket of each SWA in turn to identify the one that reads more when the 'fault' current flows. Please check Zs first of course.


    Caveat, I may not have the right mental picture of the installation .

    It is of course silly to ask why are they not labelled, and what the official emergency isolation process is.

    Mike.
Reply
  • Are all the SWA cables the same diameter and make ? if you can see the jackets you may be able to reduce the scope for error.

    If you are brave you could try injecting a modest current onto the armour - ideally you'd need to lift the earth at the load end and that may not be possible or safe.

    However,  assuming the armour is the CPC, or at least part of the CPC, then  pulling an L-E fault current of a few amps ought to allow the correct SWA to be isolated with nothing more than  a clamp meter over the jacket of each SWA in turn to identify the one that reads more when the 'fault' current flows. Please check Zs first of course.


    Caveat, I may not have the right mental picture of the installation .

    It is of course silly to ask why are they not labelled, and what the official emergency isolation process is.

    Mike.
Children
No Data