This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Safe Disconnection to Undertake Work.

Scene. An old farm building now used as a double glazing frame maker's workshop.


The supply comes from an old shed about 40 metres away, where the meter is. The old shed has some 70s/80s rusty M.E.M. isolators that feed several S.W.A. cables that exist the shed in many directions underground. I suspect that one feeds the main farmhouse, another a rented cottage and the others various farm buildings. There is no clear labelling of the isolators.


What is the best way to locate the frame maker's  building supply where I have to work?


Somewhere I have a circuit i/d set, if I can find it, but that will need access to the live parts and I do not wish to turn off the wrong isolator.


Z.


Parents
  • I still don't understand a pair of cottages with an earth adjacent to the transformer and no other. DNO says PME, so that must be what it is.
Reply
  • I still don't understand a pair of cottages with an earth adjacent to the transformer and no other. DNO says PME, so that must be what it is.
Children
No Data