Chris Pearson:
I still don't understand a pair of cottages with an earth adjacent to the transformer and no other. DNO says PME, so that must be what it is.
The DNO might prefer you to treat it as if it were PME so that they are then free to alter it to real PME in the future. That seems to be the general advise these days for "presented as TN-S" supplies - treat them as if they could be PME.
Also if there's a CNE between the first electrode and the consumer's N-PE link, then it's TN-C-S anyway and all the dangers of a broken CNE would apply just as if it were a proper PME system with multiple electrodes on the distribution system.
- Andy.
AJJewsbury:Chris Pearson:
I still don't understand a pair of cottages with an earth adjacent to the transformer and no other. DNO says PME, so that must be what it is.The DNO might prefer you to treat it as if it were PME so that they are then free to alter it to real PME in the future. That seems to be the general advise these days for "presented as TN-S" supplies - treat them as if they could be PME.
Also if there's a CNE between the first electrode and the consumer's N-PE link, then it's TN-C-S anyway and all the dangers of a broken CNE would apply just as if it were a proper PME system with multiple electrodes on the distribution system.
No CNE, just a pair of aerial singles to a JB under the eaves. Supply then goes to each cottage where N splits into N and E in the service head. Originally, it was a single cottage and barn.
No CNE, just a pair of aerial singles to a JB under the eaves. Supply then goes to each cottage where N splits into N and E in the service head. Originally, it was a single cottage and barn.
Huh I don't get this surely you must have an LV earth at the transformer or at least at the first pole
AJJewsbury:No CNE, just a pair of aerial singles to a JB under the eaves. Supply then goes to each cottage where N splits into N and E in the service head. Originally, it was a single cottage and barn.
Isn't the supply N single then providing both N and PE to the consumer?
OK, you could look at it that way. It still appears to be PNB serving 2 customers.