whjohnson:
I just winder if there is too much paranoia surrounding the loss of a neutral in a PME system in a built-up area. Maybe different out in the sticks, but with local substations being relatively plentiful in urban areas what is really the risk?
You could well be right. Lower risk than we perceive perhaps. I was going through a concerned phase at the time. The 14th edition used to require that single phase sockets on different phases be kept at least 2m apart. Was there really a risk if single phase appliances were supplied by sockets on different phases? What were the real life reported accidents?
Z.
Zoomup:
The 14th edition used to require that single phase sockets on different phases be kept at least 2m apart.
I knew of a technician who tried to power a high-current piece of equipment by attaching two supply leads in parallel with BS 1363 plugs and proceeded to plug it into two sockets on separate phases.
wallywombat:Zoomup:
The 14th edition used to require that single phase sockets on different phases be kept at least 2m apart.I knew of a technician who tried to power a high-current piece of equipment by attaching two supply leads in parallel with BS 1363 plugs and proceeded to plug it into two sockets on separate phases.
I feel sure that he achieved his high current! ?
Zoomup:whjohnson:
I just winder if there is too much paranoia surrounding the loss of a neutral in a PME system in a built-up area. Maybe different out in the sticks, but with local substations being relatively plentiful in urban areas what is really the risk?You could well be right. Lower risk than we perceive perhaps. I was going through a concerned phase at the time. The 14th edition used to require that single phase sockets on different phases be kept at least 2m apart. Was there really a risk if single phase appliances were supplied by sockets on different phases? What were the real life reported accidents?
Z.
Back in the days of unearthed lighting circuits I suspect that the risks were significant.
An unearthed brass light switch or pendant lamp holder was fairly low low risk in an office or factory with wooden floors.
However two such switches or lamp holders and connected to different phases (or poles of a DC supply) and within reach would be dangerous.
Hence the old regulation of one pole or phase per room, with an exception for large rooms where this was impractical, in which case different phases or poles of a DC supply were permitted if 6 feet, later 2 meters apart.
The general use of plastic lamp holders and light switches and the earthing of lighting circuits rendered the regulation pointless, and it was removed, correctly in my view.
wallywombat:Zoomup:
The 14th edition used to require that single phase sockets on different phases be kept at least 2m apart.I knew of a technician who tried to power a high-current piece of equipment by attaching two supply leads in parallel with BS 1363 plugs and proceeded to plug it into two sockets on separate phases.
Now that is stupid, whichever way you look at it.
Z.
mapj1:
real life data on lost neutral incidents was gathered for the IET by the Health and Safety Labs report here.. rare, but certainly not 'never'
The chance of injury or death is just over one in a million. Knowing my luck that will be me.
Quote from report: "Equipotential bonding will also not provide protection to a person in good direct contact with earth (for example standing on a conductive concrete floor) whilst also in contact with the enclosure of the equipment under fault conditions."
That was my potato peeling machines' concern as they sat on low tables on a wet brick floor that ran with water.
Z.