Table 41.1 Assumed Touch Voltage

Former Community Member
Former Community Member
I am a bit confused by this. Why do the disconnection times in Table 41.1 appear to be based on a touch voltage of 100 volts rather than a touch voltage of 125 volts?


For example, 110% of 230=  253 volts. Assuming L and PE are of the same size and material, indirect contact touch voltage is 126.5 volts. Would 0.33 seconds not appear more realistic?  


From IEC 61200-413


08a4a94aeb06dfa98ca1080a10a33484-huge-image-20210526170240-1.png
Parents
  • Former Community Member
    0 Former Community Member
    Zoomup:
    ProMbrooke:

    I am a bit confused by this. Why do the disconnection times in Table 41.1 appear to be based on a touch voltage of 100 volts rather than a touch voltage of 125 volts?


    For example, 110% of 230=  253 volts. Assuming L and PE are of the same size and material, indirect contact touch voltage is 126.5 volts. Would 0.33 seconds not appear more realistic?  


    From IEC 61200-413


    08a4a94aeb06dfa98ca1080a10a33484-huge-image-20210526170240-1.png


    Table 41.1 refers to MAXIMUM disconnection times.


    NOTE 1 says that disconnection is not required for protection  against electric shock, but may be required for other reasons such as protection against thermal effects. Also, a 30mA R.C.D. usually protects against dangerous electric shocks in most cases, due to its swift operating action.


    Z.


     




    Right.


    Note 1 only applies to DC touch voltages between 50 and 120 volts.


    RCDs can and do fail and should not be sole means of achieving ADS.


     


Reply
  • Former Community Member
    0 Former Community Member
    Zoomup:
    ProMbrooke:

    I am a bit confused by this. Why do the disconnection times in Table 41.1 appear to be based on a touch voltage of 100 volts rather than a touch voltage of 125 volts?


    For example, 110% of 230=  253 volts. Assuming L and PE are of the same size and material, indirect contact touch voltage is 126.5 volts. Would 0.33 seconds not appear more realistic?  


    From IEC 61200-413


    08a4a94aeb06dfa98ca1080a10a33484-huge-image-20210526170240-1.png


    Table 41.1 refers to MAXIMUM disconnection times.


    NOTE 1 says that disconnection is not required for protection  against electric shock, but may be required for other reasons such as protection against thermal effects. Also, a 30mA R.C.D. usually protects against dangerous electric shocks in most cases, due to its swift operating action.


    Z.


     




    Right.


    Note 1 only applies to DC touch voltages between 50 and 120 volts.


    RCDs can and do fail and should not be sole means of achieving ADS.


     