Table 41.1 Assumed Touch Voltage

Former Community Member
Former Community Member
I am a bit confused by this. Why do the disconnection times in Table 41.1 appear to be based on a touch voltage of 100 volts rather than a touch voltage of 125 volts?


For example, 110% of 230=  253 volts. Assuming L and PE are of the same size and material, indirect contact touch voltage is 126.5 volts. Would 0.33 seconds not appear more realistic?  


From IEC 61200-413


08a4a94aeb06dfa98ca1080a10a33484-huge-image-20210526170240-1.png
Parents
  • Former Community Member
    0 Former Community Member
    Zoomup:

    R.C.D.s have saved many lives. If they are not totally reliable then use two in series to half the perceived risk. Are M.C.B.s a hundred per cent reliable?


    Z.


    Why can't the MCB be the backup? A series RCD would either have to be in literal series, or a delayed trip type main with a higher ma threshold.


Reply
  • Former Community Member
    0 Former Community Member
    Zoomup:

    R.C.D.s have saved many lives. If they are not totally reliable then use two in series to half the perceived risk. Are M.C.B.s a hundred per cent reliable?


    Z.


    Why can't the MCB be the backup? A series RCD would either have to be in literal series, or a delayed trip type main with a higher ma threshold.