Table 41.1 Assumed Touch Voltage

Former Community Member
Former Community Member
I am a bit confused by this. Why do the disconnection times in Table 41.1 appear to be based on a touch voltage of 100 volts rather than a touch voltage of 125 volts?


For example, 110% of 230=  253 volts. Assuming L and PE are of the same size and material, indirect contact touch voltage is 126.5 volts. Would 0.33 seconds not appear more realistic?  


From IEC 61200-413


08a4a94aeb06dfa98ca1080a10a33484-huge-image-20210526170240-1.png
Parents
  • "Sluggishly? With proper loop impedance an MCB will directly unlatch and open in 1.5 cycles. An RCD on the other hand must rely on unlatching a magnet, which then triggers a larger opening mechanism. Rather complex. It can jam. Any electronics can fail."


    H.R.C. fuses can clear a fault in less than half a cycle.


    When I test 30mA R.C.D.s at 5 X I delta n, I usually get an operating time of between 15 and 22 mS. Well within the 40mS most people expect.


    643.8


    Z.


Reply
  • "Sluggishly? With proper loop impedance an MCB will directly unlatch and open in 1.5 cycles. An RCD on the other hand must rely on unlatching a magnet, which then triggers a larger opening mechanism. Rather complex. It can jam. Any electronics can fail."


    H.R.C. fuses can clear a fault in less than half a cycle.


    When I test 30mA R.C.D.s at 5 X I delta n, I usually get an operating time of between 15 and 22 mS. Well within the 40mS most people expect.


    643.8


    Z.