Table 41.1 Assumed Touch Voltage

Former Community Member
Former Community Member
I am a bit confused by this. Why do the disconnection times in Table 41.1 appear to be based on a touch voltage of 100 volts rather than a touch voltage of 125 volts?


For example, 110% of 230=  253 volts. Assuming L and PE are of the same size and material, indirect contact touch voltage is 126.5 volts. Would 0.33 seconds not appear more realistic?  


From IEC 61200-413


08a4a94aeb06dfa98ca1080a10a33484-huge-image-20210526170240-1.png
Parents
  • ProMbrooke:

    Any idea as to why IEC TR 1200-413 is retired?


    No. I've wondered too. I was surprised even when I first saw it, as I've not come across other cases of such a detailed 'technical report' devoted to explaining why certain choices were made in a standard.  Perhaps it's not fashionable now to bother with public explanations. The IEC and national standards bodies appear happy to carry on selling this retired publication at a hefty price. (IEC says 'withdrawn').

     


Reply
  • ProMbrooke:

    Any idea as to why IEC TR 1200-413 is retired?


    No. I've wondered too. I was surprised even when I first saw it, as I've not come across other cases of such a detailed 'technical report' devoted to explaining why certain choices were made in a standard.  Perhaps it's not fashionable now to bother with public explanations. The IEC and national standards bodies appear happy to carry on selling this retired publication at a hefty price. (IEC says 'withdrawn').

     