Protection When Changing CSA

I have always went by the rule " when changing (lowering) csa of cable/wire then insert protection device", and further to that the second rule was "if its only a small run perhaps <2M then first rule need not apply". 


What is experience of everybody on this?


This particular application in design phase has an incoming 95mm cable in through a a switch disconnector which requires distribution to many smaller branch circuits. usually this application for me in control panels is simple as small currents (<30A) are in use but this larger requirement means the terminations get tricky having many different wire sizes.


Thanks Folks!33eaed845ccf5afaa1f80feb683c2254-huge-distribution.png
Parents
  • Yes of course, sorry I have not explained that very well, this is within one control panel, therefore no DB board within the panel.


    The DB board for the project splits the sizes into many different control panels, and within these control panels these would be various motor sizes requiring the different wiring sizes.
Reply
  • Yes of course, sorry I have not explained that very well, this is within one control panel, therefore no DB board within the panel.


    The DB board for the project splits the sizes into many different control panels, and within these control panels these would be various motor sizes requiring the different wiring sizes.