hertzal123:
Doing a condition report where the diy tenant has gone mad with surface plastic conduit downstairs to
add extra light points to varius rooms.In the kitchen are 6 edison holders on ceiling besa boxes.Noticed polarity
was wrong on the 1st one checked.My 1st thought for a coding was C2,but the lamp would need removing to
expose the live terminals,the same as a bc lampholder,which has the same danger of touching live parts .So would C3 be more appropriate?The live terminal
contacts when the lamp is fully inserted.
Hz
Zoom has it right ... the polarity issue doesn't apply to some ES lampholders. If the lampholder complies with BS EN 60238, AND is either E14 or E27, then there is no problem. Regulation 559.5.1.206 and 643.6 (ii)..
gkenyon:hertzal123:
HzZoom has it right ... the polarity issue doesn't apply to some ES lampholders. If the lampholder complies with BS EN 60238, AND is either E14 or E27, then there is no problem. Regulation 559.5.1.206 and 643.6 (ii)..
Agreed - any vaguely modern E27/E14 lampholder won't have a metal threaded ring contact, but two contacts at the base of the holder and a plastic thread for holding the lamp base - so both the L and N are similarly recessed.