Is there no issue from a DNO perspective of joining the METs or is that generally accepted practice in this situation? It's not something I've come across before.
There may be, but more importantly BS 7671 also acknowledges the problem, in Regulation 542.1.3.3
542.1.3.3 Where a number of installations have separate earthing arrangements, any protective conductors common to any of these installations shall either be capable of carrying the maximum fault current likely to flow through them or be earthed within one installation only and insulated from the earthing arrangements of any other installation. In the latter circumstances, if the protective conductor forms part of a cable, the protective conductor shall be earthed only in the installation containing the associated protective device.
How will you rate the conductor bonding the two installations together? Can you be sure they come from the same main in the street (they probably do, but ...)?
One thing to note, you don't state whether the two installations are totally separate, or whether they share any space in the building in common. But I guess it's the case that someone could run an extension lead from one part of the building to another. If either of those is the case, and there is a risk that exposed-conductive-parts supplied from both installations could be touched simultaneously, then it does need addressing, as one of the basic rules for fault protection as part of automatic disconnection of supply is not met (Regulation 411.3.1.1, particularly my highlight below):
411.3 Requirements for fault protection
411.3.1 Protective earthing and protective equipotential bonding
411.3.1.1 Protective earthing
Exposed-conductive-parts shall be connected to a protective conductor under the specific conditions for each type of system earthing as specified in Regulations 411.4 to 411.6.
Simultaneously accessible exposed-conductive-parts shall be connected to the same earthing system individually, in groups or collectively.
Conductors for protective earthing shall comply with Chapter 54.
A circuit protective conductor shall be run to and terminated at each point in wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point.
gibb01:
Given they are both 100a TP&N I'd assume installing a 16mm G&Y as per table 54.7 between the two METs will suffice & adding a 10mm G&Y to the incoming water to the basement from the Ground floor MET (Which is already bonded via the basement MET)
If the supplies are from the same main in the street, your assumption is probably correct.
There is a reason, though, that 542.1.3.3 does not refer to Table 54.7 (or indeed anywhere else in Chapter 54).
If the supplies are not from the same LV main ... now, or at some point in the future ... then who knows what diverted neutral currents there will be? Perhaps this is why the bonding is missing upstairs?
If the supplies are from a separate transformer, this is where things start to get tricky, as you may well need to take into account HV fault currents etc. which is well outside the remit of BS 7671.
To be honest, asking the DNO is the most correct course of action ... However, they may well consider it a change of use that's not been notified, and they may want to propose some changes (at a cost).