Bonding to single building with 2 TNCS supplies

Hi,

I'm sure this has been answered before - but we've just been carrying out an EICR on a small commercial building that has a 100A 3 Ph TNCS Supply to the basement & separate 100A 3Ph TNCS supply to the ground floor. We believe it used to be to separate tenancies & has since been occupied by a single tenant. The installation has a single incoming water supply to the basement that is bonded to the basement MET, However there is no bonding from the ground floor MET onto the same water supply. 

I assume it's a simple fix of adding a 10mm from the ground floor - but just wanted to see what other views are in case i'm missing something obvious. 

Not that I believe it makes too much difference, but we believe the supplies to be fed via separate TXs as the client has mentioned one supply has stayed live whilst the other has not during a power cut. 

Thanks in advance!
Parents
  • gibb01:


    Given they are both 100a TP&N I'd assume installing a 16mm G&Y as per table 54.7 between the two METs will suffice & adding a 10mm G&Y to the incoming water to the basement from the Ground floor MET (Which is already bonded via the basement MET) 

     


    If the supplies are from the same main in the street, your assumption is probably correct.


    There is a reason, though, that 542.1.3.3 does not refer to Table 54.7 (or indeed anywhere else in Chapter 54).


    If the supplies are not from the same LV main ... now, or at some point in the future ... then who knows what diverted neutral currents there will be? Perhaps this is why the bonding is missing upstairs?


    If the supplies are from a separate transformer, this is where things start to get tricky, as you may well need to take into account HV fault currents etc. which is well outside the remit of BS 7671.



    To be honest, asking the DNO is the most correct course of action ... However, they may well consider it a change of use that's not been notified, and they may want to propose some changes (at a cost).


Reply
  • gibb01:


    Given they are both 100a TP&N I'd assume installing a 16mm G&Y as per table 54.7 between the two METs will suffice & adding a 10mm G&Y to the incoming water to the basement from the Ground floor MET (Which is already bonded via the basement MET) 

     


    If the supplies are from the same main in the street, your assumption is probably correct.


    There is a reason, though, that 542.1.3.3 does not refer to Table 54.7 (or indeed anywhere else in Chapter 54).


    If the supplies are not from the same LV main ... now, or at some point in the future ... then who knows what diverted neutral currents there will be? Perhaps this is why the bonding is missing upstairs?


    If the supplies are from a separate transformer, this is where things start to get tricky, as you may well need to take into account HV fault currents etc. which is well outside the remit of BS 7671.



    To be honest, asking the DNO is the most correct course of action ... However, they may well consider it a change of use that's not been notified, and they may want to propose some changes (at a cost).