gibb01:
Given they are both 100a TP&N I'd assume installing a 16mm G&Y as per table 54.7 between the two METs will suffice & adding a 10mm G&Y to the incoming water to the basement from the Ground floor MET (Which is already bonded via the basement MET)
If the supplies are from the same main in the street, your assumption is probably correct.
There is a reason, though, that 542.1.3.3 does not refer to Table 54.7 (or indeed anywhere else in Chapter 54).
If the supplies are not from the same LV main ... now, or at some point in the future ... then who knows what diverted neutral currents there will be? Perhaps this is why the bonding is missing upstairs?
If the supplies are from a separate transformer, this is where things start to get tricky, as you may well need to take into account HV fault currents etc. which is well outside the remit of BS 7671.
To be honest, asking the DNO is the most correct course of action ... However, they may well consider it a change of use that's not been notified, and they may want to propose some changes (at a cost).
gibb01:
Given they are both 100a TP&N I'd assume installing a 16mm G&Y as per table 54.7 between the two METs will suffice & adding a 10mm G&Y to the incoming water to the basement from the Ground floor MET (Which is already bonded via the basement MET)
If the supplies are from the same main in the street, your assumption is probably correct.
There is a reason, though, that 542.1.3.3 does not refer to Table 54.7 (or indeed anywhere else in Chapter 54).
If the supplies are not from the same LV main ... now, or at some point in the future ... then who knows what diverted neutral currents there will be? Perhaps this is why the bonding is missing upstairs?
If the supplies are from a separate transformer, this is where things start to get tricky, as you may well need to take into account HV fault currents etc. which is well outside the remit of BS 7671.
To be honest, asking the DNO is the most correct course of action ... However, they may well consider it a change of use that's not been notified, and they may want to propose some changes (at a cost).