Failed EICR

Former Community Member
Former Community Member

Hi just want to know what you guys and girls do in the following situation. 

You've carried out an EICR its failed. 

Once the remedials have been carried out do you redo the original EICR so it's Satisfactory?

Or do you fill out minor works certs and give these to the customer along with the original failed report so once cross referenced  it results in being satisfactory. 

This has been bugging me for awhile now. 

Regards TS

Parents
  • I normally do the fiddling about and disconnecting first at the consumer unit, which includes checking the tightness of terminal connections. I then visually check the consumer unit. After that I check earthing of installation  exposed conductive parts, correct socket earthing and polarity etc. That way I can pick up on any missed deficiencies at the consumer unit.

     

    Z.

Reply
  • I normally do the fiddling about and disconnecting first at the consumer unit, which includes checking the tightness of terminal connections. I then visually check the consumer unit. After that I check earthing of installation  exposed conductive parts, correct socket earthing and polarity etc. That way I can pick up on any missed deficiencies at the consumer unit.

     

    Z.