RCBO failing insulation test when switched off

Former Community Member
Former Community Member

Hi

 

I am fairly new to the trade and finding things I am unsure about, sorry for what is probably a very basic question

I have been taught that switching of an RCBO should be enough to enable a good insulation test.

When running some tests on a ring final with double pole RCBO detection yesterday I found that I had to disconnect the wires from the RCBO to get a good result. I have assumed that this is just down to the design of the RCBO and past the installation, is this the correct action?

 

Thanks

Parents
  • Basically yes, you have to disconnect the circuit to test it. All the RCBO internals are on the load side. 

Reply
  • Basically yes, you have to disconnect the circuit to test it. All the RCBO internals are on the load side. 