RCBO failing insulation test when switched off
Hi
I am fairly new to the trade and finding things I am unsure about, sorry for what is probably a very basic question
I have been taught that switching of an RCBO should be enough to enable a good insulation test.
When running some tests on a ring final with double pole RCBO detection yesterday I found that I had to disconnect the wires from the RCBO to get a good result. I have assumed that this is just down to the design of the RCBO and past the installation, is this the correct action?
  • Hi Alan,
    You'd be better posting these two posts in the “wiring and the regulations” or the “ask the community” parts of the forum. Loads of people there (particularly in wiring and regs) who'll be happy be answer.
    Cheers, Andy
  • Basically yes, you have to disconnect the circuit to test it. All the RCBO internals are on the load side.
  • Many electronic protective devices like R.C.B.O.s don't like 500 Volts being applied to them. They may be damaged, so disconnection is a good thing.
  • Your always better off testing at the board for rings if possible, be careful with insulation testing on existing circuits generally connect L&N together and test to earth at 250 volts and then 500 volts.
  • As Zoom said, also watch out for surge extension leads, neons, RCD sockets, usb sockets etc.
  • Please see about 6 mins  + into this video.
    Colin Haggett:
    Thanks for all the comments and especually the video which confirm my original ideas. I had been testing at 250v with live conductors connected but didn't know that some rcbos actually needed to be fully disconnected for the test. Fuse box hadn't labelled their units like Cranborne.