TT EARTHING WIRING MATTERS

Everything you want to know about TT earthing form the IET Wiring Matters an be found here

 

Parents
  • "the earth electrode should be installed at a depth sufficient to reach the water table of the soil to remain effective." (my emphasis) seems a bit over-zealous. Around here two or three feet down remains damp enough even during summer droughts, but as we're on a hillside the actual water table is likely to be much much deeper - probably several tens of metres - really not a practical depth.

    I might take slight issue with Fig 1 too - to my mind the consumer's electrode is part of the consumer's installation, not the supply system (e.g. isn't included in the oft quoted 21 Ohms Ze for TT systems) - so really it should be to the right of the dotted line.

       - Andy.

Reply
  • "the earth electrode should be installed at a depth sufficient to reach the water table of the soil to remain effective." (my emphasis) seems a bit over-zealous. Around here two or three feet down remains damp enough even during summer droughts, but as we're on a hillside the actual water table is likely to be much much deeper - probably several tens of metres - really not a practical depth.

    I might take slight issue with Fig 1 too - to my mind the consumer's electrode is part of the consumer's installation, not the supply system (e.g. isn't included in the oft quoted 21 Ohms Ze for TT systems) - so really it should be to the right of the dotted line.

       - Andy.