Leakage from underfloor steel conduit trench

I recently inspected an old building whose wiring is drawn in underfloor steel conduits in a trench openable from the floors above (1st and 2nd floor)., and branching of to lighting and power points.  Despite the rust as shown here, the installation is in ‘working condition’.  However, there are two concerns. 

First, water ingress from cleaning is staining the soffit/ceiling under and it's a nuisance to users. Second, the old wiring used the steel conduit system as a CPC and rust could have reduced it's effectiveness.

I have thought of covering/encasing the trench permanently but two issues arise. How to deal with draw-off points at corners and at 10m interval; and the possibility that rewiring may be rendered impossible in the future.

I would appreciate any comment from anyone who has had to reckon with this such a challenge and how they approached it.

6ef10e5c47824bb2036fbbbdb1293ace-huge-img20210927120405-1.jpg
Parents
  • could the stone covers be supposed to be sealed with mastic or tar or similar ? It probably needs someone who understands 1920s floor construction to consult. I  presume the wiring is newer, and 1960s at the oldest, - any 1920 wiring would almost certainly be unsuitable for modern conditions, so it must  been re-wired before , maybe when the floors came up then, some re-sealing idea was forgotten.

    Can you remove one of the corner elbow covers on a rusty one and see what the wires is/are  like within ? I'd be nervous of assumed ‘ working condition’  it may be nearer end of life than you realise.

    Mike

Reply
  • could the stone covers be supposed to be sealed with mastic or tar or similar ? It probably needs someone who understands 1920s floor construction to consult. I  presume the wiring is newer, and 1960s at the oldest, - any 1920 wiring would almost certainly be unsuitable for modern conditions, so it must  been re-wired before , maybe when the floors came up then, some re-sealing idea was forgotten.

    Can you remove one of the corner elbow covers on a rusty one and see what the wires is/are  like within ? I'd be nervous of assumed ‘ working condition’  it may be nearer end of life than you realise.

    Mike