Bonding

Hi All

I've come to do some work at a property which has no bonding to the gas or water supply. These services enter the house on the other side to the electric supply/CU. Supply is TNCS.

Question is can I run a single 10mm cable around the outside of the house to link to both gas and water supplies. If so can I use a black cable (with green/yellow sleeve at either end) and clip direct to the wall or does it require additional mechanical protection?

Thanks in advance ?

Parents
  • D4G: 
     

    Hi All

    I've come to do some work at a property which has no bonding to the gas or water supply. These services enter the house on the other side to the electric supply/CU. Supply is TNCS.

    Question is can I run a single 10mm cable around the outside of the house to link to both gas and water supplies. If so can I use a black cable (with green/yellow sleeve at either end) and clip direct to the wall or does it require additional mechanical protection?

    Thanks in advance ?

    Common practice is to run a green yellow in black conduit. Saves possible UV damage to cable and a chance to fit galvanised metal supporting saddles 

Reply
  • D4G: 
     

    Hi All

    I've come to do some work at a property which has no bonding to the gas or water supply. These services enter the house on the other side to the electric supply/CU. Supply is TNCS.

    Question is can I run a single 10mm cable around the outside of the house to link to both gas and water supplies. If so can I use a black cable (with green/yellow sleeve at either end) and clip direct to the wall or does it require additional mechanical protection?

    Thanks in advance ?

    Common practice is to run a green yellow in black conduit. Saves possible UV damage to cable and a chance to fit galvanised metal supporting saddles 