EIC "rated time delay" value for a 61008 type-s

good day folks

 

out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch,  what was the value  (presuming the standard has a set value/range)  used and where from ?

 

regards

Habs

 

Parents
  • not quite the same question but at say 5 times the nominal trip current,  100ms is typical , and less than 50ms is a fail and 150msec is also. From here  

     

    c20d3f904ff9d4319f8c8ce1e0e51687-original-rcd-limits.jpg

     

    If cascading earth fault relays I tend to use a rule of 3 for current and time as a starting point for modifications.

    so instant 30msec fed from sub-mains supplied by perhaps 100A circuits with protection set to 100mA 0.1second, fed by generator of a few hundred amps, earth protection set to 300mA and 0.3 seconds. There are always exceptions, but it is a place to start from .

    mike

     

Reply
  • not quite the same question but at say 5 times the nominal trip current,  100ms is typical , and less than 50ms is a fail and 150msec is also. From here  

     

    c20d3f904ff9d4319f8c8ce1e0e51687-original-rcd-limits.jpg

     

    If cascading earth fault relays I tend to use a rule of 3 for current and time as a starting point for modifications.

    so instant 30msec fed from sub-mains supplied by perhaps 100A circuits with protection set to 100mA 0.1second, fed by generator of a few hundred amps, earth protection set to 300mA and 0.3 seconds. There are always exceptions, but it is a place to start from .

    mike

     