out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
not quite the same question but at say 5 times the nominal trip current, 100ms is typical , and less than 50ms is a fail and 150msec is also. From here
If cascading earth fault relays I tend to use a rule of 3 for current and time as a starting point for modifications.
so instant 30msec fed from sub-mains supplied by perhaps 100A circuits with protection set to 100mA 0.1second, fed by generator of a few hundred amps, earth protection set to 300mA and 0.3 seconds. There are always exceptions, but it is a place to start from .
mike
not quite the same question but at say 5 times the nominal trip current, 100ms is typical , and less than 50ms is a fail and 150msec is also. From here
If cascading earth fault relays I tend to use a rule of 3 for current and time as a starting point for modifications.
so instant 30msec fed from sub-mains supplied by perhaps 100A circuits with protection set to 100mA 0.1second, fed by generator of a few hundred amps, earth protection set to 300mA and 0.3 seconds. There are always exceptions, but it is a place to start from .