good day folks

 

out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch,  what was the value  (presuming the standard has a set value/range)  used and where from ?

 

regards

Habs

 

Parents
  • Sparkingchip: 
     

    There’s a table towards of the back of the regs book , which I don’t have with me, that gives the range of the standard time delays.

    Page 363. S type 130 to 500mS. (100 to 500mA)

    Z.

Reply
  • Sparkingchip: 
     

    There’s a table towards of the back of the regs book , which I don’t have with me, that gives the range of the standard time delays.

    Page 363. S type 130 to 500mS. (100 to 500mA)